Diagnostic buffer of module CPU 315-2 DP

Order No./ Description         Component                     Version                      
6ES7 315-2AG10-0AB0           Hardware                       4                            
- - -                         Firmware                       V 2.0.10                      

Rack:                         0
Slot:                         2


Event 1 of 100:  Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.):   1005
No relevance for user (Z2): 0000  (Z3): 0000
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
11:04:02:911 pm  11/13/94


Event 2 of 100:  Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
11:04:01:809 pm  11/13/94


Event 3 of 100:  Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number:   1005
DP master affected in rack   1 and slot     8
Station number:    0, slot number:   10
Operating mode: STOP (internal)
Internal error, Incoming event
11:04:01:370 pm  11/13/94


Event 4 of 100:  Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number:   1004
DP master affected in rack   1 and slot     8
Station number:    0, slot number:   10
Operating mode: STOP (internal)
Internal error, Incoming event
11:03:40:058 pm  11/13/94


Event 5 of 100:  Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number:   1000
DP master affected in rack   1 and slot     8
Station number:    0, slot number:   10
Operating mode: STOP (internal)
Internal error, Incoming event
11:03:18:745 pm  11/13/94


Event 6 of 100:  Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number:   25
DP master system ID:      1
Log. base address of the DP slave: Input address:  2043
Log. base address of the DP master:  32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:02:57:308 pm  11/13/94


Event 7 of 100:  Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number:   24
DP master system ID:      1
Log. base address of the DP slave: Input address:  2044
Log. base address of the DP master:  32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:02:57:220 pm  11/13/94


Event 8 of 100:  Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number:   23
DP master system ID:      1
Log. base address of the DP slave: Input address:  2045
Log. base address of the DP master:  32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode